by barely a splash » Wed 27 Dec, 2006 19:45
Sounds like you have a good plan -- 2 skimmers, 2 drains, 4 return inlets, 1 dedicated cleaner attachment port.
Note that hydraulic system should be designed with ALL elements in mind -- components like skimmers, drains, returns; pump size (gpm at x ft of head loss, not merely horsepower); filter size; and possibly most important of all, pipe size.
And, with regard to drains: split suction is always a good idea (in other words, using two drains teed together). Suction entrapment is not something to mess with. If using two skimmers, you would usually run maindrain lines off front port of skimmer. This implies you have four suction outlet pipes -- two for each skimmer, if using split suction. It's OK to put two pipes from separate skimmers under each drain cover, as long as you don't exceed the rated max flow of the cover.
Best of luck to you.